MyFloridaCode.com

[Florida Code Talk] CodeTalk Digest, Vol 40, Issue 2
Jim Heise JHeise at pgtindustries.com
Wed Dec 3 11:22:31 EST 2008


I agree with Glenn about the protection required above the 60 foot
level. This code is covered in the current  FBC under Section 1609.1.2
Protection of Openings. Florida adopted this IBC code on January 25th of
2007. It states that "Glazed openings located more than 30 feet above
grade shall meet the provisions of the Small Missile Test of ASTM
E1996." However, under the Exceptions glitch just under that code, it
states ... "Glazed openings in Occupancy Category II, III, or IV
buildings located over 60 feet above the ground and over 30 feet above
aggregate surface roofs located within 1,500 feet of the building shall
be permitted to be unprotected." The intent of this code is to require
protection in windows higher than 60 feet if there is an adjoining
building nearby that may shed some wind-borne debris. In the HVHZ from
30 feet and above, small missile testing is required with no cap or
limitation. 


Jim Heise
Field / Code Specialist
PGT Industries
941-480-1600 ext. 22344
941-343-7122 (Cell)

 

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of
codetalk-request at myfloridacode.com
Sent: Tuesday, December 02, 2008 12:00 PM
To: codetalk at myfloridacode.com
Subject: CodeTalk Digest, Vol 40, Issue 2

Send CodeTalk mailing list submissions to
	codetalk at myfloridacode.com

To subscribe or unsubscribe via the World Wide Web, visit
	http://myfloridacode.com/mailman/listinfo/codetalk
or, via email, send a message with subject or body 'help' to
	codetalk-request at myfloridacode.com

You can reach the person managing the list at
	codetalk-owner at myfloridacode.com

When replying, please edit your Subject line so it is more specific than
"Re: Contents of CodeTalk digest..."


Today's Topics:

   1. Impact Windows on Hirise (Terrance Pitcher)
   2. Re: Anchoring Transformers (Glen Mast)
   3. Re: Impact Windows on Hirise (Glen Mast)
   4. Some info you may find useful (Wade Mullins)
   5. Re: Anchoring Transformers (Ken Rodgers)


----------------------------------------------------------------------

Message: 1
Date: Mon, 1 Dec 2008 20:49:28 -0500
From: "Terrance Pitcher" <ppitcher at cfl.rr.com>
Subject: [Florida Code Talk] Impact Windows on Hirise
To: <codetalk at myfloridacode.com>
Message-ID: <003301c95420$39be9dd0$0400a8c0 at D15WQ211>
Content-Type: text/plain; charset="iso-8859-1"

I was to understand that the requirement for laminated windows on tall
condos is such. 0 to 30 ft large impact. 30ft to 60ft small impact
glass. Above 60ft  I assumed you did not need impact laminated glass.
These buildings are not if the HVHZ. They are on the barrier islands of
north east fl. 120 mph zone. Above 60ft I have used 1/4 tempered glass.
I pull a permit on all jobs and have passed all inspections. But today
the inspector thought that the whole building needs to be impact if over
60ft.
Thanking all of you in advance
Terry
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20081201/f501055
a/attachment.html 


------------------------------

Message: 2
Date: Tue, 2 Dec 2008 00:27:20 -0500
From: "Glen Mast" <glenmast at comcast.net>
Subject: Re: [Florida Code Talk] Anchoring Transformers
To: "Ken Rodgers" <Ken at artisanbilt.com>, <codetalk at myfloridacode.com>
Message-ID: <1573ADF55FE64CA1BD37E7A4D131B9BE at glens>
Content-Type: text/plain; format=flowed; charset="iso-8859-1";
	reply-type=original

Lets actually look at 150mph, Exposure "C", wind loads on a transformer
that is 4'x4'x30'' tall.

ASCE7-02 would treat this transformer like a solid sign or a fencewall.
With an importance factor of 1.0 the lateral wind pressure would be 48.6
psf.
48.6 x 4 x 2.5 = 486#

If the transformer weighs 2000# and the sliding coefficient is .4 (I
don't have my ACI book here but I think that is close) then the friction
provides 800# resistance.
ASCE7 doesn't assign uplift to the tops of signs but just for arguments
sake lets assign 45psf.
45 x 4'x4' = 720# uplift
2000 - 720 = 1280#
1280 x .4 = 512# resistance


 So if your in Dade-Broward you might be able to make an argument for it
but anyplace else it appears the power company has a valid point..

glen mast
.


----- Original Message -----
From: "Ken Rodgers" <Ken at artisanbilt.com>
To: <codetalk at myfloridacode.com>
Sent: Sunday, November 30, 2008 8:09 PM
Subject: [Florida Code Talk] Anchoring Transformers


> Hello All,
>
>  I have a question about securing the large transformers (large green
> boxes) to the slab they sit on.  The power company says it does not
bolt
> these to the slab even though the box  does have bolt flanges at the 
> bottom
> for bolting.  I'm trying to find something (code or otherwise) that
states
> the requirement to actually use the supplied bolt holes to secure the
> transformer to the slab.  The power company just says that because it 
> weighs
> 2,000 lbs it's not going anywhere and thus they don't bolt it.  I
guess
> using that rationale then we don't need to bolt houses down to the
> foundation.  Any info would be greatly appreciated.
>
>
>
> Ken
>
>
>
> Ken Rodgers
>
> ArtisanBilt Construction
>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
>
http://myfloridacode.com/pipermail/codetalk/attachments/20081130/5216cb8
9/attachment.html
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk 



------------------------------

Message: 3
Date: Tue, 2 Dec 2008 00:44:17 -0500
From: "Glen Mast" <glenmast at comcast.net>
Subject: Re: [Florida Code Talk] Impact Windows on Hirise
To: "Terrance Pitcher" <ppitcher at cfl.rr.com>,
	<codetalk at myfloridacode.com>
Message-ID: <461F87A54BE34E6F93B010FE0A323370 at glens>
Content-Type: text/plain; format=flowed; charset="iso-8859-1";
	reply-type=original

You are correct with one possible exception.  If there is another tall 
building nearby that has a gravel roof or tile roof then you may have to

protect windows to a higher level.  (at least that is my understanding)

glen mast


----- Original Message ----- 
From: "Terrance Pitcher" <ppitcher at cfl.rr.com>
To: <codetalk at myfloridacode.com>
Sent: Monday, December 01, 2008 8:49 PM
Subject: [Florida Code Talk] Impact Windows on Hirise


>I was to understand that the requirement for laminated windows on tall 
>condos is such. 0 to 30 ft large impact. 30ft to 60ft small impact
glass. 
>Above 60ft  I assumed you did not need impact laminated glass. These 
>buildings are not if the HVHZ. They are on the barrier islands of north

>east fl. 120 mph zone. Above 60ft I have used 1/4 tempered glass. I
pull a 
>permit on all jobs and have passed all inspections. But today the
inspector 
>thought that the whole building needs to be impact if over 60ft.
> Thanking all of you in advance
> Terry
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
>
http://myfloridacode.com/pipermail/codetalk/attachments/20081201/f501055
a/attachment.html
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk 



------------------------------

Message: 4
Date: Tue, 2 Dec 2008 07:47:33 -0500
From: "Wade Mullins" <wadem at qualityprecast.com>
Subject: [Florida Code Talk] Some info you may find useful
To: <codetalk at myfloridacode.com>
Message-ID:
	
<6FCB0E1A41983D4B986EBAE690935450E8608B at qpfile01.qualityprecast.lan>
Content-Type: text/plain; charset="us-ascii"

 

 

Wade Mullins

Quality Precast Company

wadem at qualityprecast.com

R & R Rebar Fabricators, Inc.

wadem at rrrebar.com

Direct 813.662.5260

Mobile 813.267.8736

<mailto:wadem at qualityprecast.com>  

 

<mailto:wadem at rrrebar.com>  

 

<mailto:wadem at rrrebar.com>  

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20081202/76a13ef
0/attachment.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: News Items 12 02 08 08.doc
Type: application/msword
Size: 54784 bytes
Desc: News Items 12 02 08 08.doc
Url :
http://myfloridacode.com/pipermail/codetalk/attachments/20081202/76a13ef
0/attachment.doc 


------------------------------

Message: 5
Date: Tue, 2 Dec 2008 07:12:37 -0600
From: "Ken Rodgers" <Ken at artisanbilt.com>
Subject: Re: [Florida Code Talk] Anchoring Transformers
To: "'Glen Mast'" <glenmast at comcast.net>, <codetalk at myfloridacode.com>
Message-ID: <007101c9547f$a7019b90$f504d2b0$@com>
Content-Type: text/plain;	charset="us-ascii"

These transformers are about 6 feet tall, not 30 inches.  I appreciate
the
math lesson but I believe there are probably other things to consider
besides wind that have the ability to move a transformer.

Thanks to everyone for their inputs.  I'll press on the with info I've
received.

Ken

-----Original Message-----
From: Glen Mast [mailto:glenmast at comcast.net] 
Sent: Monday, December 01, 2008 11:27 PM
To: Ken Rodgers; codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] Anchoring Transformers

Lets actually look at 150mph, Exposure "C", wind loads on a transformer
that

is 4'x4'x30'' tall.

ASCE7-02 would treat this transformer like a solid sign or a fencewall.
With an importance factor of 1.0 the lateral wind pressure would be 48.6

psf.
48.6 x 4 x 2.5 = 486#

If the transformer weighs 2000# and the sliding coefficient is .4 (I
don't 
have my ACI book here but I think that is close) then the friction
provides 
800# resistance.
ASCE7 doesn't assign uplift to the tops of signs but just for arguments
sake

lets assign 45psf.
45 x 4'x4' = 720# uplift
2000 - 720 = 1280#
1280 x .4 = 512# resistance


 So if your in Dade-Broward you might be able to make an argument for it
but

anyplace else it appears the power company has a valid point..

glen mast
.


----- Original Message ----- 
From: "Ken Rodgers" <Ken at artisanbilt.com>
To: <codetalk at myfloridacode.com>
Sent: Sunday, November 30, 2008 8:09 PM
Subject: [Florida Code Talk] Anchoring Transformers


> Hello All,
>
>  I have a question about securing the large transformers (large green
> boxes) to the slab they sit on.  The power company says it does not
bolt
> these to the slab even though the box  does have bolt flanges at the 
> bottom
> for bolting.  I'm trying to find something (code or otherwise) that
states
> the requirement to actually use the supplied bolt holes to secure the
> transformer to the slab.  The power company just says that because it 
> weighs
> 2,000 lbs it's not going anywhere and thus they don't bolt it.  I
guess
> using that rationale then we don't need to bolt houses down to the
> foundation.  Any info would be greatly appreciated.
>
>
>
> Ken
>
>
>
> Ken Rodgers
>
> ArtisanBilt Construction
>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
>
http://myfloridacode.com/pipermail/codetalk/attachments/20081130/5216cb8
9/at
tachment.html
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk 




------------------------------

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
http://myfloridacode.com/mailman/listinfo/codetalk


End of CodeTalk Digest, Vol 40, Issue 2
***************************************


This e-mail/electronic communication and any attachments that accompany it (the "Communication") may contain information that is privileged, confidential, or proprietary and is intended solely for the use of the individual(s) to whom it was meant to be addressed.  If you have received this Communication by mistake, or you are not the intended recipient, please be advised that any disclosure, dissemination, distribution, copying, or other use or retention of this Communication or its substance is prohibited.  If you have received this Communication in error, please contact me immediately.  You are also requested to destroy any copies or print-outs and to permanently delete this Communication, in its entirety, from your computer. Thank you.
For additional information about our company, please visit our website at http://www.pgtindustries.com




More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |