Glen that is a field solution but I would still require a letter from
the manufacturer before attempting to fasten to a glued in buck. There
are other issues affecting the drainage plane in the veneer as well that
could create some liability for he window installer. Again, the proper
way to install a replacement window in this application is to cut the
drywall back to allow the thicker window to be inset enough to gain
proper transfer of loads to the framing.

I spent about 20 years selling as a wholesaler and then as a contractor
supervising installation of replacement windows, my recommendations are
based on sound installation that complies with recommendations contained
in many manufacturers detail instructions and drawings. I am sure PGT
would agree with the recommendation to insure the window gets a good
bite in the buck.


Darius H Grimes CRC, CSI, CDT
Executive Director of Operations
SkyeTec
9570 Regency Sq Blvd Suite 410
Jacksonville, FL 32225
dgrimes at skyetec.com
Cell (904) 662-6707
 
Mitigation is.........the effort to reduce loss of life and property by
lessening the impact of disasters.

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of
codetalk-request at myfloridacode.com
Sent: Monday, November 17, 2008 12:00 PM
To: codetalk at myfloridacode.com
Subject: CodeTalk Digest, Vol 39, Issue 15

Send CodeTalk mailing list submissions to
	codetalk at myfloridacode.com

To subscribe or unsubscribe via the World Wide Web, visit
	http://myfloridacode.com/mailman/listinfo/codetalk
or, via email, send a message with subject or body 'help' to
	codetalk-request at myfloridacode.com

You can reach the person managing the list at
	codetalk-owner at myfloridacode.com

When replying, please edit your Subject line so it is more specific than
"Re: Contents of CodeTalk digest..."


Today's Topics:

   1. Re: Window Replacement with Brick veneer (Glen Mast)
   2. Re: CodeTalk Digest, Vol 39, Issue 14 (Darius Grimes)
   3. Re: Window Replacement with Brick veneer (Jim)


----------------------------------------------------------------------

Message: 1
Date: Sun, 16 Nov 2008 15:20:22 -0500
From: "Glen Mast" <glenmast at comcast.net>
Subject: Re: [Florida Code Talk] Window Replacement with Brick veneer
To: <bradsproducts at bellsouth.net>, "Terrance Pitcher"
	<ppitcher at cfl.rr.com>,	<codetalk at myfloridacode.com>
Message-ID: <C24FAE917E4D48889EB0EADAF99CEE7F at glens>
Content-Type: text/plain; format=flowed; charset="iso-8859-1";
	reply-type=original

Terrance:  Your inspector is correct.  bd had a good idea and that is
filling the void.  I would run this past the inspector or a plans
reviewer before doing it but here is what I would suggest.  Using a
fairly dry piece of  pt, plane it down so that it will fit snugly in the
void.  Apply a generous bead of adhesive (PL premium urethane is a good
one) to both the wood wall and the backside of the brick.  Slide filler
piece into place.

hope that works for ya,

glen mast

----- Original Message -----
From: <bradsproducts at bellsouth.net>
To: "Terrance Pitcher" <ppitcher at cfl.rr.com>;
<codetalk at myfloridacode.com>
Sent: Sunday, November 16, 2008 8:34 AM
Subject: Re: [Florida Code Talk] Window Replacement with Brick veneer


> Your inspector is likely correct about drilling new holes,. as all of 
> these building parts such as windows have been approved for their use
with 
> their engineering. Ya, common sense would say drill and it would work 
> great, but if it fails with the next storm, who ya gonna call. It
(like 
> everything else)  boils down to liability. Why can't you just fill the

> void? Hope this helps.
> --
> bd
> www.bradsfinewoodproducts.com
> -------------- Original message from "Terrance Pitcher" 
> <ppitcher at cfl.rr.com>: -------------- 
>
> I have a frame building with a brick veneer It has a 1" space between
the 
> two. The inspector is not allowing the window to be installed because
of 
> the void. he says the window must be supported fully for the 3.5
inches of 
> the window thickness. The outside is supported by the veneer and the 
> inside is supported by the drywall and the double studs underneath.The

> void is where the screw holes are located.We wanted to drill other
holes 
> in further to catch the studs and he
>> said he needs engineering from the manufacture PGT to allow this
change.
>> -------------- next part -------------- 
>> An HTML attachment was scrubbed... URL: 
>>
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/bf66e13
e/attach
>> ment.html
>> _______________________________________________
>> CodeTalk mailing list
>> CodeTalk at myfloridacode.com
>> Unsubscribe or change your options at:
>> http://myfloridacode.com/mailman/listinfo/codetalk
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
>
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/2e66a10
1/attachment.html
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk 



------------------------------

Message: 2
Date: Sun, 16 Nov 2008 23:39:40 +0000
From: "Darius Grimes" <dgrimes at skyetec.com>
Subject: Re: [Florida Code Talk] CodeTalk Digest, Vol 39, Issue 14
To: codetalk at myfloridacode.com
Message-ID:
	
<99957033-1226878786-cardhu_decombobulator_blackberry.rim.net-1961903044
- at bxe109.bisx.prod.on.blackberry>
	
Content-Type: text/plain

The proper way to install this is to cut the drywall back to allow the
window to come into the structure where it can be properly mounted.
Filling the void will not transfer the load to the framing properly and
under negative pressure will trnsfer the load to the veneer which is not
part of the MWFRS.
Sent via BlackBerry from T-Mobile

-----Original Message-----
From: codetalk-request at myfloridacode.com

Date: Sun, 16 Nov 2008 12:00:01 
To: <codetalk at myfloridacode.com>
Subject: CodeTalk Digest, Vol 39, Issue 14


Send CodeTalk mailing list submissions to
	codetalk at myfloridacode.com

To subscribe or unsubscribe via the World Wide Web, visit
	http://myfloridacode.com/mailman/listinfo/codetalk
or, via email, send a message with subject or body 'help' to
	codetalk-request at myfloridacode.com

You can reach the person managing the list at
	codetalk-owner at myfloridacode.com

When replying, please edit your Subject line so it is more specific
than "Re: Contents of CodeTalk digest..."


Today's Topics:

   1. Window Replacement with Brick veneer (Terrance Pitcher)
   2. Re: Window Replacement with Brick veneer
      (bradsproducts at bellsouth.net)


----------------------------------------------------------------------

Message: 1
Date: Sun, 16 Nov 2008 08:13:49 -0500
From: "Terrance Pitcher" <ppitcher at cfl.rr.com>
Subject: [Florida Code Talk] Window Replacement with Brick veneer
To: <codetalk at myfloridacode.com>
Message-ID: <001e01c947ed$2cba5500$0400a8c0 at D15WQ211>
Content-Type: text/plain; charset="iso-8859-1"

I have a frame building with a brick veneer It has a 1" space between
the two. The inspector is not allowing the window to be installed
because of the void. he says the window must be supported fully for the
3.5 inches of the window thickness. The outside is supported by the
veneer and the inside is supported by the drywall and the double studs
underneath.The void is where the screw holes are located.We wanted to
drill other holes in further to catch the studs and he said he needs
engineering from the manufacture PGT to allow this change.
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/bf66e13
e/attachment.html


------------------------------

Message: 2
Date: Sun, 16 Nov 2008 13:34:52 +0000
From: bradsproducts at bellsouth.net
Subject: Re: [Florida Code Talk] Window Replacement with Brick veneer
To: "Terrance Pitcher" <ppitcher at cfl.rr.com>,
	<codetalk at myfloridacode.com>
Message-ID:
	
<111620081334.6399.4920217C000711C3000018FF22218683269B0A02D2089B9A019C0
4040A0DBF9C9B0C9A0B019D9F9C0B0E9D0D at att.net>

Content-Type: text/plain; charset="us-ascii"

Your inspector is likely correct about drilling new holes,. as all of
these building parts such as windows have been approved for their use
with their engineering. Ya, common sense would say drill and it would
work great, but if it fails with the next storm, who ya gonna call. It
(like everything else)  boils down to liability. Why can't you just fill
the void? Hope this helps.
--
bd
www.bradsfinewoodproducts.com
-------------- Original message from "Terrance Pitcher"
<ppitcher at cfl.rr.com>: --------------

I have a frame building with a brick veneer It has a 1" space between
the two. The inspector is not allowing the window to be installed
because of the void. he says the window must be supported fully for the
3.5 inches of the window thickness. The outside is supported by the
veneer and the inside is supported by the drywall and the double studs
underneath.The void is where the screw holes are located.We wanted to
drill other holes in further to catch the studs and he
> said he needs engineering from the manufacture PGT to allow this
change.
> -------------- next part --------------
> An HTML attachment was scrubbed... URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/bf66e13
e/attach
> ment.html
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/2e66a10
1/attachment.html


------------------------------

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
http://myfloridacode.com/mailman/listinfo/codetalk


End of CodeTalk Digest, Vol 39, Issue 14
****************************************



------------------------------

Message: 3
Date: Sun, 16 Nov 2008 21:14:13 -0600 (CST)
From: Jim <jimfahs at younginspections.com>
Subject: Re: [Florida Code Talk] Window Replacement with Brick veneer
To: Terrance Pitcher <ppitcher at cfl.rr.com>, codetalk at myfloridacode.com
Message-ID: <1534786.1226891653495.JavaMail.root at web02>
Content-Type: text/plain; charset="us-ascii"

I'd say, simply work with PGT engineering,  My experience has been 
that window company engineering departments are very accessible.  
You are fortunate in this case you are working with a Florida 
company - they will understand you more readily than 
out-of-staters.




On Sun Nov 16 07:13:49 CST 2008, Terrance Pitcher 
<ppitcher at cfl.rr.com> wrote:

> I have a frame building with a brick veneer It has a 1" space 
> between the two. The inspector is not allowing the window to be 
> installed because of the void. he says the window must be 
> supported fully for the 3.5 inches of the window thickness. The 
> outside is supported by the veneer and the inside is supported by 
> the drywall and the double studs underneath.The void is where the 
> screw holes are located.We wanted to drill other holes in further 
> to catch the studs and he said he needs engineering from the 
> manufacture PGT to allow this change.
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
>
http://myfloridacode.com/pipermail/codetalk/attachments/20081116/bf66e13
e/attachment.html 
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk
> 
> 
> 


------------------------------

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
http://myfloridacode.com/mailman/listinfo/codetalk


End of CodeTalk Digest, Vol 39, Issue 15
****************************************




More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |