[Florida Code Talk] Existing Roof Mounted unit
Mark Cramer mcramer1 at tampabay.rr.com
Wed Nov 19 18:57:27 EST 2008


Agreed.

509.1  General.
Existing mechanical systems undergoing alteration shall comply with Section
301.11 of the Florida Building Code, Mechanical. 

(Note that the definition of level 1 alteration includes replacement of
existing equipment.)

301.11 Repair.
Defective material or parts shall be replaced or repaired in such a manner
so as to preserve the original approval or listing.


Mark Cramer
Mark Cramer Inspection Services, Inc.
492 20th Ave. 
Indian Rocks Beach, FL 33785
727-595-4211
http://www.BestTampaInspector.com




-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Glen Mast
Sent: Wednesday, November 19, 2008 6:02 PM
To: Dan Griffin; codetalk at myfloridacode.com
Cc: jan_leggettheatingandair at comcast.net; Cheryl Harris at FRACCA
Subject: Re: [Florida Code Talk] Existing Roof Mounted unit

Here is my take on it........

You are performing a Level 1 alteration.  The code says that you can not 
make the building less safe or less energy efficient than it already is.
You can not install a  unit that weighs more than 105% of the  prior unit 
without evaluating the structure supporting the replaced equipment.
Assuming that you are not doing any of the above then you should be able to 
mount the new unit to the existing support ......... unless the new 
equipment is not designed for that type of support.

as always jmho,

glen mast



----- Original Message ----- 
From: "Dan Griffin" <Daniel at weatherengineers.com>
To: <codetalk at myfloridacode.com>
Cc: <jan_leggettheatingandair at comcast.net>; "Cheryl Harris at FRACCA" 
<Charris at FRACCA.org>
Sent: Wednesday, November 19, 2008 11:52 AM
Subject: [Florida Code Talk] Existing Roof Mounted unit


>I have a question as the code is being interpreted between 2 counties as
> different.
>
> We have a condensing unit located on a residential roof 20 years old &
> we changed it out & secured it to the existing timbers. The county the
> change out is in says we must raise the unit to a stand, now on 4x4's.
> Another county says if we were in their county we can put it back where
> it was on 4x4's.
>
> I read the code & understand, we would only raise the unit if the job was:
>
> 1. New construction or
> 2. If we were relocating it from the ground to the roof (never been on
> the roof before).
>
> Please set us straight & tell me the truth.
>
> Thanks, Dan
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk 

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk




More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |