[Florida Code Talk] Guard Bottom Rail Clearance
Jeff Hyde Jeff at ContractorsInstitute.com
Fri Jan 23 09:41:01 EST 2009


All;

Open guards shall have balusters or ornamental patterns such that a 4"
diameter sphere cannot pass through.  The bottom rail rejection of a 2"
diameter sphere left the code 6 or 7 years ago.  The triangular opening
formed between the riser, tread and bottom rail shall reject the 6"
sphere. Elevated walkways used for access to electrical, mechanical or
plumbing equipment shall have guards that reject the 21" diameter
sphere.  

Jeff 

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of
WPMyrick at aol.com
Sent: 2009-01-23 09:20
To: rsanders at usanova.com
Cc: codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] Guard Bottom Rail Clearance

 
Thanks, Roger.
 
That does make sense. 6" is a pretty big opening. It seems that I can  
remember having a problem with an inspector on one of my houses a long
time  ago 
about that rule. (6" v. 4").
although my concrete stoop was only about 14" above grad  Does  anyone 
remember when that 4" v. 6" rule changed?
 
Paul
 
Building & Zoning Code Violation Resolutions
W. Paul Myrick, Pres.,CEO, CBC, BBA 
Florida Certified  Design-Build Contractor  CBC023304

               
William Paul Myrick Properties Incorporated
192 Ivy Lakes Drive, St.  Johns, Florida 32259
Phone & Fax Number: (904) 829-6829
Nextel: 838-2398 Direct Connect:160+34+1064  
Web site at _http://hometown.aol.com/wpmyrick/_ 
(http://hometown.aol.com/wpmyrick/)  
respond via email: _wpmyrick at aol.com_ (mailto:wpmyrick at aol.com) 


 
 
In a message dated 1/23/2009 9:04:28 A.M. Eastern Standard Time,  
rsanders at usanova.com writes:

That's what the  spacing used to be 6" but kids where sticking their
heads 
through the  balusters at the top of stairs and falling off the step and

breaking their  necks. So they switched it to 4" spacing .  
 
Regards,

Roger W. Sanders  CBO,PX,BN,ER
Sr. Code  Consultant
Nova Engineering  & Environmental,LLC.
5808  D Breckenridge Parkway
Tampa Fl.  33610
Phone: 813-623-3100
Fax: 813-623-3545
 
  
____________________________________
 
From:  WPMyrick at aol.com [mailto:WPMyrick at aol.com] 
Sent: Thursday, January 22, 2009 4:15  PM
To: Roger  Sanders
Subject: Re:  [Florida  Code Talk] Guard Bottom Rail Clearance
 
 
Roger,
 

 
Where does the 6"s  come in?
 

 
Paul
 

 

 

 
In a message dated  1/22/2009 3:52:33 P.M. Eastern Standard Time, 
rsanders at usanova.com  writes:

80% of 1 year old  children's heads will pass through a 6" gap none will
pass through a 4"  gap, similar basis for up to 3 year olds as I
recall.

Regards,

Roger W. Sanders CBO,PX,BN,ER
Sr. Code  Consultant
Nova Engineering & Environmental,LLC.
5808 D Breckenridge  Parkway
Tampa Fl. 33610
Phone:  813-623-3100
Fax:  813-623-3545

 




**************A Good Credit Score is 700 or Above. See yours in just 2
easy 
steps! 
(http://pr.atwola.com/promoclk/100000075x1215855013x1201028747/aol?redir
=http://www.freecreditreport.com/pm/default.aspx?sc=668072%26hmpgID=62%2
6bcd=De
cemailfooterNO62)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090123/109883a
0/attachment.html 
_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk




More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |