Here is the section from the 2004 Res. code See my comments at the end. R602.8 Fireblocking required. Fireblocking shall be provided to cut off all concealed draft openings (both vertical and horizontal) and to form an effective fire barrier between stories, and between a top story and the roof space. Fireblocking shall be provided in wood-frame construction in the following locations. 1. In concealed spaces of stud walls and partitions, including furred spaces and parallel rows of studs or staggered studs; as follows: 1.1. Vertically at the ceiling and floor levels. 1.2. Horizontally at intervals not exceeding 10 feet (3048 mm). 2. At all interconnections between concealed vertical and horizontal spaces such as occur at soffits, drop ceilings and cove ceilings. 3. In concealed spaces between stair stringers at the top and bottom of the run. Enclosed spaces under stairs shall comply with Section R311.2.2. 4. At openings around vents, pipes, and ducts at ceiling and floor level, with an approved material to resist the free passage of flame and products of combustion. 5. For the fireblocking of chimneys and fireplaces, see Section R1001.16. 6. Fireblocking of cornices of a two-family dwelling is required at the line of dwelling unit separation. R602.8.1 Materials. Except as provided in Section R602.8, Item 4, fireblocking shall consist of 2-inch (51 mm) nominal lumber, or two thicknesses of 1-inch (25.4 mm) nominal lumber with broken lap joints, or one thickness of 23/32-inch (19.8 mm) wood structural panels with joints backed by 23/32-inch (19.8 mm) wood structural panels or one thickness of ¾-inch (19.1 mm) particleboard with joints backed by ¾-inch (19.1 mm) particleboard, ½-inch (12.7 mm) gypsum board, or ¼-inch (6.4 mm) cement-based millboard. Batts or blankets of mineral wool or glass fiber or other approved materials installed in such a manner as to be securely retained in place shall be permitted as an acceptable fire block. Batts or blankets of mineral or glass fiber or other approved non-rigid materials shall be permitted for compliance with the 10 foot horizontal fireblocking in walls constructed using parallel rows of studs or staggered studs. Loose-fill insulation material shall not be used as a fireblock unless specifically tested in the form and manner intended for use to demonstrate its ability to remain in place and to retard the spread of fire and hot gases. R602.8.1.1 Unfaced fiberglass. Unfaced fiberglass batt insulation used as fireblocking shall fill the entire cross section of the wall cavity to a minimum height of 16 inches (406 mm) measured vertically. When piping, conduit or similar obstructions are encountered, the insulation shall be packed tightly around the obstruction. R602.8.1.2 Fireblocking integrity. The integrity of all fireblocks shall be maintained. The code is really for draft stopping (not fire stopping which is a totally different matter) The draft that they are worried about is from a small fire that would be contained in the cavity between the studs. If the product of combustion (CO2 mostly) can be kept inside of the cavity the fire will self extinguish in a relatively short period of time (most likely no one would even know it had been there except for the short that caused it). The problem you are experiencing is from no-one knowing exactly how much heat to expect from this intra-cavity fire. While the foam is an excellent draft stop at low temperatures it might melt at higher temperatures. The counties that are asking for fire caulking know that it will handle the worst case scenario. Since this is a national issue the manufacturers of one of the foams might want to apply to ICC or NFPA for a ruling if they feel their foam is up to the challenge. Might make a good science fair project. glen ----- Original Message ----- From: Dave Forrest To: CodeTalk at myfloridacode.com Sent: Tuesday, July 21, 2009 9:39 PM Subject: [Florida Code Talk] Penetrations through interior frame top plates,one story single fm If anyone can refer me to the code-book-page on this subject I would appreciate it. The purpose for filling these top plate penetrations is for fire stop. Different counties are stating different types of foam and or caulk for this. One county says the yellow foam from Home Depot in the can is acceptable. While another county wants foam or caulk to have a fire rating label on the label. Question is does the caulking have to be fire rated and if so where is that in the code?(the penetrations are from electric wiring and vent stacks) Thanks in advance for your help. ------------------------------------------------------------------------------ _______________________________________________ CodeTalk mailing list CodeTalk at myfloridacode.com Unsubscribe by sending an email to codetalk-unsubscribe at myfloridacode.com or Unsubscribe or change your options at: http://myfloridacode.com/mailman/listinfo/codetalk -------------- next part -------------- An HTML attachment was scrubbed... URL: http://myfloridacode.com/pipermail/codetalk/attachments/20090721/b7220203/attachment.html
- Previous message: [Florida Code Talk] Penetrations through interior frame top plates, one story single fm
- Next message: [Florida Code Talk] draft stopping
- Messages sorted by: [ date ] [ thread ] [ subject ] [ author ]
More information about the CodeTalk mailing list