It is "supposed" to be at the top of the ceiling, but if wall mounted it
MUST be within 4" & 12" (down) from the ceiling (to the top of the
detector). (If on ceiling - not within 4" of any wall.) 2007 - National
Fire Alarm Code Handbook Pg. #156 Section 5.7.3.2.1

Mark Tardif
fidratfire at mindspring.com
President & Qualifier
Fidrat Fire & Systems, Inc.
305-596-3588 Ofc./Fax #
305-898-5126 Mb.#


> [Original Message]
> From: <Marquisconst at aol.com>
> To: <WR290 at aol.com>; <codetalk at myfloridacode.com>
> Date: 6/8/2009 3:46:52 PM
> Subject: Re: [Florida Code Talk] smoke detectors
>
> Tom;
>  
> actually it is for a house; the opinions vary from 12" to 36" for a wall  
> mounted SD in a vaulted room
>  
> Chris Kavala
> Marquis Const. & Dev. Inc. _www.southernsips.com_ 
> (http://www.southernsips.com/) 
> 3714 Covington Drive
> Holiday, Florida  34691
> Toll Free ............................. 1-877-321-SIPS
> main: (727)  937-3090
> fax (727) 937-1849
> cell (727) 243-2717
>
> FL. LIC. #  CBC036455 
> (residential / commercial)
> LA. LIC. # CL.0033845  (commercial GC)
> GA. LIC. # RLCO000624 (residential / light  commercial GC)
> **************Download the AOL Classifieds Toolbar for local deals at
your 
> fingertips. 
>
(http://toolbar.aol.com/aolclassifieds/download.html?ncid=emlcntusdown000000
04)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090608/ebfa47d5/at
tachment.html 
> _______________________________________________
> CodeTalk mailing list
> CodeTalk at myfloridacode.com
> Unsubscribe or change your options at:
> http://myfloridacode.com/mailman/listinfo/codetalk





More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |