MyFloridaCode.com

[Florida Code Talk] CodeTalk Digest, Vol 45, Issue 14
Jon Cole joncole999 at cfl.rr.com
Wed May 27 12:23:49 EDT 2009


Well, I have tried to unsubscribe from these emails 4 times during the past 2 months by following the procedure at the bottom of the screen, but I still get 10-15 emails a day from this forum...

I'm going to try doing a reply to all from every email I get and see if someone there will get sick of it and actually remove me from the distribution list as I've requested.

jc.


-----Original Message-----
From: codetalk-bounces at myfloridacode.com [mailto:codetalk-bounces at myfloridacode.com] On Behalf Of WR290 at aol.com
Sent: Tuesday, May 26, 2009 11:40 AM
To: havenm at palmbayflorida.org; Bob at contractorsinstitute.com; Marquisconst at aol.com; codetalk at myfloridacode.com
Subject: [Norton AntiSpam] Re: [Florida Code Talk] CodeTalk Digest, Vol 45, Issue 14

 
Dear _havenm at palmbayflorida.org_ (mailto:havenm at palmbayflorida.org) 
 
This is also an educational forum. If you have fact that an approved  
testing agency has sheet metal as a fire barrier. Can you please send this forum  
a copy. 
 
Thank you
Tom Ricci
BT Builders Inc
 
 
 
In a message dated 5/26/2009 11:29:39 A.M. Eastern Daylight Time,  
havenm at palmbayflorida.org writes:

What you  believe (Mr. Koning) and what an approved testing agency says may 
be a  difference of opinion.

-----Original Message-----
From:  codetalk-bounces at myfloridacode.com 
[mailto:codetalk-bounces at myfloridacode.com]  On Behalf Of Bob Koning
Sent: Tuesday, May 26, 2009 9:07 AM
To:  marquisconst at aol.com; codetalk at myfloridacode.com
Subject: Re: [Florida Code  Talk] CodeTalk Digest, Vol 45, Issue 14

I believe it is. I think it  would have more burn time than 1/2" drywall


R.J.Koning -  Director
Contractors Institute
rjkoning at contractorsinstitute.com
8301  Joliet Street
Hudson, Fl  34667
727-863-5147




-----Original Message-----
From:  codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com]  On Behalf Of
marquisconst at aol.com
Sent: Tuesday, May 26, 2009 6:06  AM
To: codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk]  CodeTalk Digest, Vol 45, Issue 14

I don't think sheetmetal is a fire  barier?


-----Original Message-----
From:  codetalk-request at myfloridacode.com
To: codetalk at myfloridacode.com
Sent:  Mon, 25 May 2009 12:41 pm
Subject: CodeTalk Digest, Vol 45, Issue  14



Send CodeTalk mailing list submissions to
codetalk at myfloridacode.com

To subscribe or unsubscribe via the World  Wide Web, visit
http://myfloridacode.com/mailman/listinfo/codetalk
or, via email, send a  message with subject or body 'help' to
codetalk-request at myfloridacode.com

You can reach the person managing  the list at
codetalk-owner at myfloridacode.com

When  replying, please edit your Subject line so it is more specific
than "Re:  Contents of CodeTalk digest..."


Today's Topics:

1. Re: Questionable call by Building official (WR290 at aol.com)
2. Re: Questionable call by Building official  (WR290 at aol.com)


----------------------------------------------------------------------

Message:  1
Date: Mon, 25 May 2009 12:38:45 EDT
From: WR290 at aol.com
Subject:  Re: [Florida Code Talk] Questionable call by Building
official
To: dalemarcialee at sprintmail.com, gyantorn at scgov.net,
pathoag at cfl.rr.com, jcoughlin at englehomes.com,  FineR at gtlaw.com,
noleball at hotmail.com,    codetalk at myfloridacode.com
Message-ID:  <bea.3de02de0.374c2395 at aol.com>
Content-Type: text/plain;  charset="utf-8"


Hi Dale

Missed you last weekend. Hope all is  well.

Relating to your post. The plain language R309.2 does not mention  fire
protection, only separation, to the ceiling of a garage unless there  is
a
habitable area above.  Although we do know that 1/2 GWB is 20  minute.
That is
why the interpretation from BOAF states No.

See  below

>From BOAF Informal Interpretation

Question:

Is  it the intent of R309.1 and R309.2 to be applied to attic  accesses
in
garages with relation to a fire rating?
Answer:
No.  The requirement is  for separation as stipulated, not a fire  rated
assembly. The attic access  closure
would need to be  equivalent to 1/2 inch gyp board, or in the case  where

there is a  habitable area above the
ceiling, 5/8 inch Type X gyp board  (where  the ceiling is used to
provide
the  separation).
Commentary:
Section  309.1 addresses openings between  the garage and the residence.
Section 309.2  establish
es  the
separation requirement between the garage and the attic. 1/2   inch
gypsum
is allowed.


In a message dated 5/25/2009 11:02:50  A.M. Eastern Daylight Time,
dalemarcialee at sprintmail.com  writes:

I'm  unclear as to the installation of the ladder. Is it a  fixed ladder
through the  scuttle hole creating a penetration of the  ceiling
assembly?
R309.2 requires  ceiling protection of 1/2 " gdw  on the ceiling and if
its a
floor/ceiling  assembly,( with  habitable space above) it must be 5/8
type "X'.
If the ladder  and  scuttle create a penetration through the ceiling
envelope,
it must  be  protected in some manner.
Most pull-down attic ladders are not  fire-rated  but a layer of
sheet-metal
or drywall applied to the  bottom side is usually  accepted.

Dale Lee,CBO
Bay Harbor  Islands

-----Original  Message-----
>From:  WR290 at aol.com
>Sent: May 23, 2009 3:26  PM
>To:  gyantorn at scgov.net, pathoag at cfl.rr.com,   jcoughlin at englehomes.com,
FineR at gtlaw.com, noleball at hotmail.com,   codetalk at myfloridacode.com
>Subject: Re: [Florida Code Talk]   Questionable call by Building
official
>
>
>I think he  said  he discussed it with the BO because he might want  to
be
one
> in the   future,
>
>Tom
>
>
>a message dated   5/23/2009 3:23:20 P.M. Eastern Daylight Time,
>gyantorn at scgov.net   writes:
>
>This  issue is getting out of hand. Discuss  with  the BO and inspector.

You
>may be   suprised.
>
>-----  Original Message  -----
>From:    codetalk-bounces at myfloridacode.com
><codetalk-bounces at myfloridacode.com>
>To:   WR290 at aol.com  <WR290 at aol.com>;  jcoughlin at englehomes.com
><jcoughlin at englehomes.com>;  FineR at gtlaw.com   <FineR at gtlaw.com>;
noleball at hotmail.com
><noleball at hotmail.com>;  codetalk at myfloridacode.com
<codetalk at myfloridacode.com>
>Sent:  Sat May 23 15:15:06   2009
>Subject: Re: [Florida Code Talk]  Questionable call by  Building
official
>
>Your backing  down does nothing but to  propagate the problem   state
wide.
>
>-----Original   Message-----
>From:    codetalk-bounces at myfloridacode.com
>[mailto:codetalk-bounc
es at myfloridacode.com]    On Behalf Of WR290 at aol.com
>Sent: Saturday, May 23, 2009 2:32   PM
>To:  jcoughlin at englehomes.com; FineR at gtlaw.com;    noleball at hotmail.com;
>codetalk at myfloridacode.com
>Subject:  Re:  [Florida  Code Talk] Questionable call by  Building
official
>
>
>I absolutely   understand.
>
>This is purely a business decision.  If he  want  to  take this official

on.
>He will not get a CO,  His bank will  keep  charging for extensions of
his
>loan.  Assuming he has  a loan. And  probably 2 years down the road  he
might
>get
>this issue done. What I see  is FR paint  and a GFCI > The  total cost
is
>less
>
>than  100.00.
>
>I have been down this road and it is not pretty. Not  to  mention that
this
>person is a contractor. I assume he  will  want to continue to   work
with
this
>
>building  department.
>
>
>Tom
>
>
>In a   message dated  5/23/2009 2:21:22 P.M. Eastern Daylight  Time,
>jcoughlin at englehomes.com writes:
>
>The  problem  with  rolling  over when you are right and the  inspector
won't
>listen  is  sort of  like a dog  humping your leg. If you let the  dog
hump
>you,
>
>he  always  will and you will  be his  biatch.
>
>Go to the BO first, then  get  BIA  involved.  This will work 95% of  the

time.
>
>Rolling over is  NOT  an    Option.
>
>________________________________
>
>From:    WR290 at aol.com
>To: Jay Coughlin; FineR at gtlaw.com ;    noleball at hotmail.com ;
>codetalk at myfloridacode.com
>Sent:   Sat May  23 14:16:18 2009
>Subject: Re:  [Florida Code  Talk]  Questionable call  by  Building
official

>
>
>Charles:
>
>I was  not going to  chime  in on this.This is a  common happening.  You
can
>do
>one of  two  things. Take a recorder  with you and  tell him you are
>recording
>his   comments, send his comments along with  a  complaint to DBPR.  Or
you
>can
>just make the  repairs and go one with life.  I  would absolutly
recommend

>the second  option.
>
>Tom Ricci CBO
>BT   Builders   Inc
>
>In a message dated 5/21/2009 8:44:12 A.M.  Eastern  Daylight   Time,
>jcoughlin at englehom
es.com   writes:
>
>This is typical of   some rouge  inspectors.  Call the CBO and it goes
away
>if not  in  book,  can be  resolved in one day  normally.
>
>-----Original    Message-----
>From:     codetalk-bounces at myfloridacode.com
>[mailto:codetalk-bounces at myfloridacode.com]    On Behalf Of
FineR at gtlaw.com
>Sent: Wednesday, May 20, 2009   7:55   PM
>To: noleball at hotmail.com;    codetalk at myfloridacode.com
>Subject:  Re: [Florida Code  Talk]   Questionable call by  Building
official
>
>(This is not  intended to be legal  advice)
>
>If it were  me, and my  county had a board of  rules and appeals, I
would
>file an   appeal.  In my  experience, the filing of  an appeal is enough

to
>lead to a  discussion that frequently  resolves the matter  without   the
>hearing being  necessary.  And if it  doesn't get  resolved,  you have a
set
>date by which the matter  will  be resolved.    If  your county   does
not
>have  such a board, you can use the  binding   interpretation process in

Fla
>Stat 553.775  which is very  fast.
>
>Good   luck
>
>Robert
>
>Robert S. Fine,   Esq.,    AIA
>
>
>-----------------------------------------------------------------------
-
>--
>Tax    Advice Disclosure: To ensure  compliance with  requirements
>imposed  by  the IRS under  Circular 230,  we inform you that any  U.S.
>federal tax  advice   contained in this communication  (including   any
>attachments),  unless otherwise specifically  stated, was  not  intended
or
>written to be used, and cannot be  used,  for the purpose of  (1)
avoiding
>penalties under the   Internal Revenue Code or (2)    promoting,
marketing
or
>recommending to another party any   matters  addressed  herein.
>
>The  information  contained in this  transmission  may contain
>privileged and  confidential information.  It is intended only  for  the
use
>of the person(s) named  above. If you are not the   intended  recipient,
you
>are  hereby notified that any  review,   dissemination, distribution  or
>duplication of  this  communication is  strictly  prohibited. If you  are
not
>the  intende
d recipient, please   contact  the sender by reply email and
>destroy all copies of the   original  message. To reply to our  email
>administrator   directly, please send an  email     to
>mailto:postmaster at gtlaw.com.
>
>-----------------------------------------------------------------------
-
>--
>
>
>From:    codetalk-bounces at myfloridacode.com
><codetalk-bounces at myfloridacode.com>
>To:   codetalk at myfloridacode.com  <codetalk at myfloridacode.com>
>Sent: Wed  May  20  19:35:05 2009
>Subject: [Florida Code Talk]   Questionable  call by  Building official
>
>
>
>I  am  trying to obtain a C.O. for a   residence we have completed  and
the
>building official has  taken some  liberties with  his  judgement.  I
>usually try  to do what is  asked  of me by  the building officials as I
>will   likely be one one day but   this one is taking it a bit  far.
>
>
>
>We have  installed an    attic ladder (aluminum ladder) in the garage
and
>the   inspector  refuses to issue a C.O. until the attic  ladder  and
hatch
>is painted with  fire resistant paint.    Further, he insists that  we
>install GFCI  receptacles in  the  dining room (not kitchen)  which is
not
>required  by  the  N.E.C. or the Florida Building  Code.  I took  the
book
to
>him  and asked for him to show  it to me  and he said that  it is not in

the
>Code but it is in   "his code" and it is  what he wants to  see.   He
insists
>that the house will not  pass until the hatch  is  painted with fire
>retardant paint and the  recepatcles in  the dining room  (not  kitchen)

are
>changed.
>
>
>
>To make  matters worse,  he  is the electrical inpector  for  the
>jurisdiction and is  not licensed  to do any other   inspections.  Does
>anyone  have any suggestions  on  this  one?  Soem of you are  building
>officials on here  and  may  be able to help me   out.
>
>
>
>Charles    Walker
>
>CW  Building Contractor,  inc
>
>CBC  1250992    CCC 1325996 CFC  1427782
>
>_________________________________________________________________
>Windows    Live(tm): Keep your life in    sync.
>http://windowslive.
com/explore?ocid=TXT_TAGLM_BR_life_in_synch_052009
>--------------    next part --------------
>An HTML  attachment was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090520/781efb
c
>2/attachment.html
>_______________________________________________
>CodeTalk    mailing  list
>CodeTalk at myfloridacode.com
>Unsubscribe  or  change your options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>-----    Original Message    -----
>
>_______________________________________________
>CodeTalk   mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>_______________________________________________
>CodeTalk    mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>
>
>
>
>________________________________
>
>Recession-proof   vacation ideas. Find free things to do in the  U.S.

><http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
c
>ntustra
>v00000002>
>--------------  next part --------------
>An HTML attachment  was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090523/e45fd8
35/a
t
>tachment.html
>_______________________________________________
>CodeTalk   mailing    list
>CodeTalk at myfloridacode.com
>Unsubscribe  or change your  options     at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>**************Recession-proof    vacation ideas.  Find free things to do
in
>the  U.S.
>(http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
c
>ntustrav00000002)
>--------------    next part --------------
>An HTML attachment was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090523/608c0d
2d/a
t
>tachment.html
>_______________________________________________
>CodeTalk   mailing  list
>CodeTalk at myfloridacode.com
>Unsubscribe  or  change your options    at:
>http://myfloridacode.com/mailman/
listinfo/codetalk
>
>_______________________________________________
>CodeTalk    mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>**************Recession-proof   vacation ideas.  Find free things to do
in
>the  U.S.
>(http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
cntustrav00000002)
>--------------   next part --------------
>An HTML attachment was  scrubbed...
>URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090523/3c67ce4
1/attachment.html

>_______________________________________________
>CodeTalk   mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your options   at:
>http://myfloridacode.com/mailman/listinfo/codetalk





**************We  found the real ?Hotel California? and the ?Seinfeld?
diner. What will you  find? Explore  WhereItsAt.com.
(http://www.whereitsat.com/?ncid=emlwenew00000004)
--------------  next part --------------
An HTML attachment was  scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090525/cb308d6
d/attachment.html


------------------------------

Message:  2
Date: Mon, 25 May 2009 12:40:27 EDT
From: WR290 at aol.com
Subject:  Re: [Florida Code Talk] Questionable call by Building
official
To: WR290 at aol.com, dalemarcialee at sprintmail.com,  gyantorn at scgov.net,
pathoag at cfl.rr.com,  jcoughlin at englehomes.com, FineR at gtlaw.com,
noleball at hotmail.com, codetalk at myfloridacode.com
Message-ID:  <cdc.4bdb0b26.374c23fb at aol.com>
Content-Type: text/plain;  charset="utf-8"

In a message dated 5/25/2009 12:38:45 P.M. Eastern  Daylight Time, WR290

writes:

Hi Dale

Missed you last  weekend. Hope all is well.

Relating to your post. The plain language  R309.2 does not mention fire
protection, only separation, to the ceiling of  a garage unless there is
a
habitable area above.  Although we do  know that 1/2 GWB is 20  minute.
That is
why the interpretation  from BOAF states No.

See below

>From BOAF Informal  Interpretatio
n

Question:

Is it the intent of R309.1 and  R309.2 to be applied to attic accesses
in
garages with relation to a  fire rating?
Answer:
No. The requirement  is for separation as  stipulated, not a fire rated
assembly. The attic access  closure would  need to be equivalent to 1/2
inch gyp
board, or in the case  where  there is a habitable area above the
ceiling,
5/8 inch Type X gyp  board  (where the ceiling is used to provide  the
separation).





Commentary:
Section 309.1  addresses openings between the garage  and the residence.
Section  309.2 establishes the separation requirement  between the  garage
and
the attic. 1/2 inch gypsum is  allowed.


Tom  Ricci
BT Builders Inc



In a message dated 5/25/2009 11:02:50  A.M. Eastern Daylight Time,
dalemarcialee at sprintmail.com  writes:

I'm  unclear as to the installation of the ladder. Is it a  fixed ladder
through  the scuttle hole creating a penetration of the  ceiling
assembly?
R309.2  requires ceiling protection of 1/2 " gdw  on the ceiling and if
its a
floor/ceiling assembly,( with habitable  space above) it must be 5/8 type
"X'.
If the ladder and scuttle create a  penetration through the ceiling
envelope, it must be protected in some  manner.
Most pull-down attic  ladders are not fire-rated but a layer  of
sheet-metal
or drywall applied to  the bottom side is usually  accepted.

Dale Lee,CBO
Bay Harbor  Islands

-----Original  Message-----
>From:  WR290 at aol.com
>Sent: May 23, 2009 3:26  PM
>To:  gyantorn at scgov.net, pathoag at cfl.rr.com,  jcoughlin at englehomes.com,

FineR at gtlaw.com, noleball at hotmail.com,   codetalk at myfloridacode.com
>Subject: Re: [Florida Code Talk]   Questionable call by Building
official
>
>
>I think  he  said he discussed it with the BO because he might want  to
be
one
> in  the  future,
>
>Tom
>
>
>a message dated   5/23/2009 3:23:20 P.M. Eastern Daylight Time,
>gyantorn at scgov.net  writes:
>
>This  issue is  getting out of hand. Discuss  with the BO and inspector.

You
>may  be   surprised.
>
>----- Original Message   -----
>From:   co
detalk-bounces at myfloridacode.com
><codetalk-bounces at myfloridacode.com>
>To:   WR290 at aol.com  <WR290 at aol.com>;  jcoughlin at englehomes.com
><jcoughlin at englehomes.com>;  FineR at gtlaw.com   <FineR at gtlaw.com>;
noleball at hotmail.com
><noleball at hotmail.com>;  codetalk at myfloridacode.com
<codetalk at myfloridacode.com>
>Sent:  Sat May 23 15:15:06   2009
>Subject: Re: [Florida Code Talk]  Questionable call by  Building
official
>
>Your backing  down does nothing but to  propagate the problem   state
wide.
>
>-----Original   Message-----
>From:    codetalk-bounces at myfloridacode.com
>[mailto:codetalk-bounces at myfloridacode.com]    On Behalf Of
WR290 at aol.com
>Sent: Saturday, May 23, 2009 2:32   PM
>To:  jcoughlin at englehomes.com; FineR at gtlaw.com;    noleball at hotmail.com;
>codetalk at myfloridacode.com
>Subject:  Re:  [Florida  Code Talk] Questionable call by  Building
official
>
>
>I absolutely   understand.
>
>This is purely a business decision.  If he  want   to take this official

on.
>He will not get a CO,  His bank will  keep  charging for extensions of
his
>loan.  Assuming he  has a loan. And  probably 2 years down the road  he
might
>get
>this issue done. What I see  is FR paint  and a GFCI > The  total cost
is
>less
>
>than  100.00.
>
>I have been down this road and it is not pretty. Not  to  mention that
this
>person is a contractor. I assume he   will want to continue to   work
with
this
>
>building   department.
>
>
>Tom
>
>
>In a    message dated 5/23/2009 2:21:22 P.M. Eastern Daylight  Time,
>jcoughlin at englehomes.com writes:
>
>The   problem  with rolling  over when you are right and the  inspector
won't
>listen is  sort of  like a dog humping  your leg. If you  let the dog
hump
>you,
>
>he   always  will and  you will be his biatch.
>
>Go to the  BO first, then  get  BIA  involved. This will work 95% of  the

time.
>
>Rolling  over is  NOT an    Option.
>
>________________________________
>
>From:    WR290 at aol.com
>To: Jay Coughlin; FineR at gtlaw.com ;    noleball at hotmail.com ;
>codetalk at myfloridacode.com
>Sent:
Sat  May  23 14:16:18 2009
>Subject: Re:   [Florida Code Talk]  Questionable call  by  Building
official

>
>
>Charles:
>
>I was  not going to   chime in on this.This is a  common happening.  You
can
>do
>one of two  things. Take a recorder with you  and  tell him  you are
>recording
>his  comments,  send his comments  along with a  complaint to DBPR.  Or
you
>can
>just  make the repairs and go one with life.  I  would absolutly
recommend
>the second  option.
>
>Tom Ricci  CBO
>BT  Builders   Inc
>
>In a message dated  5/21/2009 8:44:12 A.M. Eastern  Daylight   Time,
>jcoughlin at englehomes.com  writes:
>
>This is typical  of   some rouge  inspectors. Call the CBO and it goes
away
>if not  in  book,  can be resolved in one day   normally.
>
>-----Original    Message-----
>From:     codetalk-bounces at myfloridacode.com
>[mailto:codetalk-bounces at myfloridacode.com]    On Behalf Of
FineR at gtlaw.com
>Sent: Wednesday, May 20, 2009   7:55   PM
>To: noleball at hotmail.com;    codetalk at myfloridacode.com
>Subject:  Re: [Florida Code   Talk]  Questionable call by Building
official
>
>(This is  not intended to be legal advice)
>
>If it were  me, and my  county had a board of rules and  appeals, I
would
>file an   appeal.  In my experience,  the filing of  an appeal is  enough
to
>lead to a discussion  that frequently  resolves  the matter without  the
>hearing  being  necessary.   And if it doesn't get resolved,  you have
a
set
>date by  which the matter will be resolved.     If  your  county  does
not
>have such a board, you can use  the  binding   interpretation process in
Fla
>Stat 553.775   which is very  fast.
>
>Good   luck
>
>Robert
>
>Robert S. Fine,   Esq.,    AIA
>
>
>-----------------------------------------------------------------------
-
>--
>Tax    Advice Disclosure: To ensure  compliance with   requirements
>imposed by  the IRS under  Circular 230,  we  inform you that any U.S.
>federal tax  advice   contained in  this communication (including   any
>attachments),  unless  otherwise specifically stated, was  not  intended
or
>
written to  be used, and cannot be  used, for the purpose of  (1)
avoiding
>penalties under the  Internal Revenue Code or (2)    promoting,
marketing  or
>recommending to another party any   matters   addressed herein.
>
>The  information  contained in this  transmission  may contain
>privileged and  confidential  information. It is intended only  for the

use
>of the  person(s) named above. If you are not the   intended   recipient,
you
>are hereby notified that any   review,   dissemination, distribution or
>duplication of   this  communication is  strictly prohibited. If you  are

not
>the  intended recipient, please  contact the  sender by  reply email and
>destroy all copies of the  original  message. To  reply to our  email
>administrator  directly, please send an   email     to
>mailto:postmaster at gtlaw.com.
>
>-----------------------------------------------------------------------
-
>--
>
>
>From:    codetalk-bounces at myfloridacode.com
><codetalk-bounces at myfloridacode.com>
>To:   codetalk at myfloridacode.com  <codetalk at myfloridacode.com>
>Sent:  Wed May  20  19:35:05 2009
>Subject: [Florida Code Talk]   Questionable  call by  Building  official
>
>
>
>I am  trying to obtain a C.O. for  a   residence we have completed  and
the
>building official  has  taken some  liberties  with his judgement.   I
>usually try  to do what is  asked  of me by the building  officials as I
>will   likely be one one day but  this one is  taking it a bit  far.
>
>
>
>We have installed  an    attic ladder (aluminum ladder) in the garage
and
>the   inspector  refuses to issue a C.O. until the attic  ladder  and
hatch
>is painted with  fire resistant paint.    Further, he insists that  we
>install GFCI  receptacles  in  the dining room (not kitchen)  which is
not
>required  by   the N.E.C. or the Florida Building  Code.  I took  the
book
to
>him  and asked for him to show  it to me  and he said  that it is not in

the
>Code but it is in   "his code" and it  is what he wants to  see.   He
insists
>that the house will  not pass until the hatch  is  painted with
fire
>retardant paint  and the recepatcles  in the dining room  (not  kitchen)

are
>changed.
>
>
>
>To make  matters worse,  he  is the electrical inpector  for  the
>jurisdiction and is  not licensed  to do any other   inspections.   Does
>anyone have any suggestions  on  this  one?  Some  of you are building
>officials on here  and  may  be able to  help me  out.
>
>
>
>Charles    Walker
>
>CW  Building Contractor,  inc
>
>CBC  1250992    CCC 1325996 CFC  1427782
>
>_________________________________________________________________
>Windows    Live(tm): Keep your life in    sync.
>http://windowslive.com/explore?ocid=TXT_TAGLM_BR_life_in_synch_052009
>--------------    next part --------------
>An HTML  attachment was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090520/781efb
c
>2/attachment.html
>_______________________________________________
>CodeTalk    mailing  list
>CodeTalk at myfloridacode.com
>Unsubscribe  or  change your options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>-----    Original Message    -----
>
>_______________________________________________
>CodeTalk   mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>_______________________________________________
>CodeTalk    mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>
>
>
>
>________________________________
>
>Recession-proof   vacation ideas. Find free things to do in the  U.S.

><http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
c
>ntustra
>v00000002>
>--------------  next part --------------
>An HTML attachment  was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090523/e45fd8
35/a
t
>tachment.html
>_______________________________________________
>CodeTalk   mailing    list
>CodeTalk at myfloridacode.com
>Unsubscribe  or change your  options     at:
>http:/
/myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>**************Recession-proof    vacation ideas.  Find free things to do
in
>the  U.S.
>(http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
c
>ntustrav00000002)
>--------------    next part --------------
>An HTML attachment was    scrubbed...
>URL:
>http://myfloridacode.com/pipermail/codetalk/attachments/20090523/608c0d
2d/a
t
>tachment.html
>_______________________________________________
>CodeTalk   mailing  list
>CodeTalk at myfloridacode.com
>Unsubscribe  or  change your options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>_______________________________________________
>CodeTalk    mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your  options    at:
>http://myfloridacode.com/mailman/listinfo/codetalk
>
>
>
>
>**************Recession-proof   vacation ideas.  Find free things to do
in
>the  U.S.
>(http://travel.aol.com/travel-ideas/domestic/national-tourism-week?ncid
=eml
cntustrav00000002)
>--------------   next part --------------
>An HTML attachment was   scrubbed...
>URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090523/3c67ce4
1/attachment.html

>_______________________________________________
>CodeTalk   mailing list
>CodeTalk at myfloridacode.com
>Unsubscribe or  change  your options   at:
>http://myfloridacode.com/mailman/listinfo/codetalk






____________________________________
We  found the real 'Hotel California' and



**************We found  the real ?Hotel California? and the ?Seinfeld?
diner. What will you find?  Explore  WhereItsAt.com.
(http://www.whereitsat.com/?ncid=emlwenew00000004)
--------------  next part --------------
An HTML attachment was  scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090525/07c046b
5/attachment.html


------------------------------

_______________________________________________
CodeTalk  mailing  list
CodeTalk at myfloridacode.com
http://myfloridacode.com/mailman/listinfo/codetalk


End  of CodeTalk Digest, Vol 45, Issue  14

****************************************

-------------- next  part --------------
An HTML attachment was  scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20090526/78df03c
2/attachment.html
_______________________________________________
CodeTalk  mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your  options  at:
http://myfloridacode.com/mailman/listinfo/codetalk

_______________________________________________
CodeTalk  mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your  options  at:
http://myfloridacode.com/mailman/listinfo/codetalk

CONFIDENTIALITY  NOTICE:

The information contained in this email is strictly  confidential and 
prepared solely for the use of the intended recipient(s). The  copyright of this 
communication belongs to the City of Palm Bay.  If you  are not the intended 
recipient, please do not read, use, disseminate,  distribute or copy this 
message or attachments.If you have received this  message in error, please 
notify the sender immediately and delete this  message. Views expressed in 
this message are those of the individual sender,  and are not necessarily the 
views of the City of Palm Bay City  Council.

DISCLAIMER:

Before opening any attachments, please  check them for viruses and 
defects.The sender does not accept liability for  any viruses, errors or omissions 
in the contents of this message or  attachment, which arise as a result of 
email  transmission.

_______________________________________________
CodeTalk  mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your  options  at:
http://myfloridacode.com/mailman/listinfo/codetalk


 
**************We found the real Hotel California and the Seinfeld 
diner. What will you find? Explore WhereItsAt.com. 
(http://www.whereitsat.com/?ncid=emlwenew00000004)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://myfloridacode.com/pipermail/codetalk/attachments/20090526/53547809/attachment.html 
_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk






More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |