[Florida Code Talk] FW: Summary Report - FBC Meeting - 2010.06.08
Rob Harrell rharrell1 at cfl.rr.com
Sun Jul 11 17:40:03 EDT 2010


 
-----Original Message-----
From: Florida Building Code [mailto:codes at floridabuilding.org] 
Sent: Friday, June 25, 2010 3:17 PM
Subject: Summary Report - FBC Meeting - 2010.06.08



FLORIDA BUILDING COMMISSION

June 8, 2010 MEETING

SUMMARY REPORT 

 

The detailed “Facilitator’s Report” is located at:

 <http://www.dca.state.fl.us/fbc/commission/1_commission_meetings.htm>
http://www.dca.state.fl.us/fbc/commission/1_commission_meetings.htm

or

 <http://consensus.fsu.edu/FBC/fbc_reports.html>
http://consensus.fsu.edu/FBC/fbc_reports.html

 

 

Next Meeting of the Commission:

 

            August 10, 2010, Crowne Plaza Hotel, Melbourne Beach,
Florida

 

NOTICE:       The Commission’s Technical Advisory Committees will
consider proposed amendments to the 2009 International Code in Rule
Development Workshops during July and August 2010. The schedule of
meetings and proposed amendments to be considered by each TAC can be
found on the Commission’s website at:

 

 
<http://www.dca.state.fl.us/fbc/thecode/2010_Code_Development/2010_TAC_S
chedule.htm>
http://www.dca.state.fl.us/fbc/thecode/2010_Code_Development/2010_TAC_Sc
hedule.htm

 

 

 

Major Business and Actions at June 8, 2010 meeting:

 

The Commission approved the TAC rule development workshop process and
schedule for developing recommendations and the Commission’s rule
adoption hearing process for ruling on proposed 2010 Florida Building
Code amendments. Routine business was conducted as follows.

 

Workplan Update:    See the “Facilitator’s Report”

 

Product Approvals: See the “Facilitator’s Report”

 

Accessibility Code Waivers:     See the “Facilitator’s Report” for
waiver analysis.

 

1.	Pine Creek Sporting Club

Issue:  Vertical accessibility to the upper levels of a tree house
structure.

Action:  Withdrawn at the request of the applicant.

2.	Superstein Building, 350 Euclid Avenue, Miami Beach

Issue:   Vertical accessibility to all three floors of a historic
building containing an apartment and 11 hotel units. Accessible guest
rooms provided on first floor.

Action:            Waiver granted.

3.	University of South Florida Basketball Training Facility, 4202
E. Fowler Avenue, Tampa

Issue:   Vertical accessibility to three rows of tiered seating in the
film room of a basketball training facility.  Accessible seating is
provided in the first row.

Action:            Waiver granted.

4.	Hollywood Golf, 6000 Universal Boulevard, Orlando

Issue:   Vertical accessibility to 9 holes of a new 36 hole miniature
golf course. The course is designed to permit persons with mobility
impairments to play nine holes of golf with alternate pin/hole
placements to provide the experience of playing a total of 18 holes in
both courses in the project.

Action: Waiver granted.

5.	Hernando Elementary K, 12124 Commercial Way, Weeki Wachee

Issue:   Vertical accessibility to all rows of seats in a collapsible
bleacher system in a gymnasium. Seven wheelchair seating locations are
provided on the first level of the bleachers.

Action: Waiver granted.

6.	Orange County Orlando Magic Recreation Center – Mildred Dixon
Site, 303 S. W. Crown Point Road, Winter Garden

Issue:   Vertical accessibility to all rows of seats in a retractable
bleacher system located in a new, $5,000,000 facility. The 213 seat
bleacher system will provide 6 wheelchair seating locations with
companion seats at the lower level bleachers.

Action: Waiver granted.

7.	Whispering Pines Center, 609 S. W. 89th Avenue, Miramar

Issue:   Modify the 18” maneuvering clearance at a doorway and to reduce
the size of a toilet room grab bar from 42” to 36” due to a structural
column in this existing facility.  

Action: Dismiss. Commission cannot waive federal requirement but
building official may make determination that compliance is “technically
infeasible”.

8.	Winter Park Community Center, 721 W. New England Avenue, Winter
Park

Issue:   Vertical accessibility to all rows of seats in a new
retractable bleacher system.  Current retractable bleacher system
provides accessible seating on first two rows.

Action: Waiver granted.

9.	Alpha Delta Pi Sorority House Corporation, 537 West Jefferson
Street, Tallahassee

Issue:   Vertical accessibility to the second floor of a 14,239 square
foot building that was constructed in 1970. Renovation is to a second
floor bathroom.

Action: Waiver granted.

10.	KIPP School, 1440 McDuff Avenue North, Jacksonville

Issue:   Vertical accessibility to all rows of an existing cast concrete
bleacher system in a former greyhound racing facility that is being
converted to a charter school interior auditorium.  Eight wheelchair
locations are provided at the top of auditorium.

Action: Approved with conditions.

11.	Kids Inc. Daycare Facility, 1410 West Indianhead Drive,
Tallahassee

Issue:   Vertical accessibility to platform levels in day care facility
located in a church 

Action: Approved with conditions.

12.	Florida State University – Johnston Building, 143 Honors Way,
Tallahassee

Issue:   Vertical accessibility to all rows of seats in a classroom
expansion of a building constructed in 1932. Classroom has 6 stepped
platforms with 95 fixed seats and 4 additional wheelchair locations at
top and bottom levels.  

Action: Approved with conditions.

13.	Soho Beach House, 4385 Collins Avenue, Miami Beach

Issue:   Vertical accessibility to second floor of historic hotel where
waiver had been granted for use of space as guest rooms but now space
intended to be used for offices.

Action:            Waiver approved.

14.	Greenview Hotel, 1671 Washington Avenue, Miami Beach

Issue:   Elevator with interior dimensions in compliance with the
current code for a historic building. 

Action: Waiver granted.

 

 

Declaratory Statements/Interpretations:     See the “Facilitator’s
Report” and the Commission and TAC/POC meeting Agendas online for
additional information:
http://www.dca.state.fl.us/fbc/commission/1_commission_meetings.htm

 

Second Hearings – Final

 

DCA09-DEC-259 by Robert S. Fine Counsel for Malibu Lodging Investments,
LLC. – 

Q:        Does attachment of lightweight mural materials to existing
building facades require a permit.        

Action:  Deferred

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_1209/Commission/First_Hea
ring/DEC-351.pdf> DCA09-DEC-411 by Manny Sanchez of Fenestration Testing
Laboratory, Inc. – 

Q#1:    Do windows have to be tested in three samples in size,
configuration and glazing?.

A:        Yes. According to section 1714.6 a minimum of three
specimens/samples must be tested for the product in question.

Q#2:    As the testing laboratory agency for the State are we correct in
making such

determination as to what was tested is ample or not and is in
compliance.

A:        Yes. The test laboaratory is responsible to test according to
the applicable standards.

 Action:   Approved

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_0410/Commission/First_Hea
ring/DCA10-DEC-002.html> DCA10-DEC-002 by Derrek Runion of GreenBuilt,
Inc. 

Q:        When a system is engineered for a custom home or commercial
building consistent with FBC Section 2210 is the system exempt from
“product approval” pursuant to Florida Product Approval rule 9B-72.030
exceptions?

Note: The petitioner had variations on question #1. All answers were the
same.

A:        Yes. To the extent the system is a “custom /one of a kind” it
falls outside the scope of the optional state approval.  Approval may be
achieved through local building plans review and inspection.

Action:   Approved

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_0410/Commission/First_Hea
ring/DCA10-DEC-034.html> DCA10-DEC-034 by C.W. (Ben) Bentley 

Q:        Does the 2007 Florida Building Code [Residential] allow
installation of a PRV [pressurerelief] only valve in the “solar loop”
portion of a solar water heating system? 

A:        YES.  As long as there is a temperature and pressure valve
provided at the storage tank to protect the potable water delivery
section.  

Action:   Approved

 

First Hearings

 

DCA10-DEC-038 by Ray Habic of Gillette Generators

Q: Are generator housings subject to the minimum wind requirements of
the Code?

Action: Dismissed

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_0610/Code_Admin/DCA10-DEC
-059_Putnam_Co.pdf> DCA10-DEC-059 by Paul T. Myers, Building Official of
Putnam County

Q:        Do Florida Statute 553.73 and the 2007 Florida Building Code
Section 102.2 exempt the construction of a new building or addition to,
alteration or change of use of an existing building on a farm to be used
for: (1) making and bottling wine from farm raised grapes, (2) the
processing of farm raised fish, (3) receiving the public for purchase of
off-site services, (4) equestrian arena, stables, barns for non-farm
activities/events, and (5) an office for farm use.

Action: Deferred

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_0610/Roofing_TAC/South_Da
ytona_DCA10-DEC-079.pdf> DCA10-DEC-079 by Richard Mihalich. Chief
Building Official of City of South Daytona

Q #.1.  Can a new modified bitumen roofing system be installed over the
existing roof coverings without the addition of the required minimum
slope of ¼” in 12” for roofing covering systems requiring that minimum
slope?

Q#.2. Does evaporation of standing water within 48 hours meet the
definition of Positive Roof Drainage?

Action: Deferred

 

DCA-DEC-085 by Paul E. Radauskus, C.B.O. Building Official of Sarasota
County

Action: Withdrawn by Applicant

 

DCA-DEC-091 by George Merlin of George Merlin Associates, Inc.

Action: Dismissed

 

 
<http://www.dca.state.fl.us/fbc/commission/FBC_0610/Code_Admin/DCA10-DEC
-107_Putnam_County.pdf> DCA10-DEC-107 by Pual T. Myers, Building
Official of Putnam County.

Action: Dismissed

 

 

 

 

 

-------------- next part --------------