[Florida Code Talk] CodeTalk Digest, Vol 59, Issue 30
Eric Haefli eric.haefli.bqed at statefarm.com
Wed Jul 21 13:47:03 EDT 2010


I wasn't clear.  In order to indicate Answer A on Question #2 on the
UMVIF, an asphalt shingle roof covering has to meet the following
conditions:

1) the requirements of 2001 FBC or 1994 SFBC 
2) have a product approval listing
3) and it must have passed 110-mph or greater test (ASTM D3161 enhanced
for 110-mph or ASTM D7158 F,G, or H rating, or TAS 100-95 and TAS
107-95) (FYI- there really isn't any F rating for ASTM D7158, it's an
error on the UMVIF)

Since the 2001 FBC, 2004 FBC, and 2007 FBC all allow asphalt shingles
tested at wind speeds less than 110-mph in certain geographic regions,
my intent was to point out that the testing requirements are also
important to confirm when completing the UMVIF.  The inspector cannot
simply rely on being code-compliant to the 2001 FBC or 1994 SFBC.

Eric

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Mark Cramer
Sent: Wednesday, July 21, 2010 11:13 AM
To: codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] CodeTalk Digest, Vol 59, Issue 30

Not exactly. The code says: Shingles classified as ASTM D 3161 Class F,
TAS107 or ASTM D 7158 are acceptable for use in all wind zones.

The Wind Mit form says: At a minimum meets the 2001 Florida Building
Code or
the 1994 South Florida Building Code and has a Miami-Dade NOA or FBC
2001
Product Approval listing demonstrating compliance with ASTM D 3161
(enhanced
for 110 MPH) OR ASTM D, 7158 (F, G or H), OR FBC TAS 100-95 and TAS
107-95,
OR FMRC 4470 and/or 4471 (for metal roofs).

As an example, a Tamko Heritage 30 shingle is warranted for 80 MPH when
nailed with four nails, yet it meets the listed standards (on the wind
mit
form) and could be installed in any wind zone. 

Mark Cramer
Mark Cramer Inspection Services, Inc.
492 20th Ave. 
Indian Rocks Beach, FL 33785
727-595-4211
http://www.BestTampaInspector.com


Mark Cramer
Mark Cramer Inspection Services, Inc.
492 20th Ave. 
Indian Rocks Beach, FL 33785
727-595-4211
http://www.BestTampaInspector.com


-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Eric Haefli
Sent: Wednesday, July 21, 2010 11:25 AM
To: Jack; codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] CodeTalk Digest, Vol 59, Issue 30

I agree with what Mr. Harris writes, but I thought, in addition to the
stated code-compliance, the asphalt shingles would also be required to
have
passed one of the tests listed at 110-mph or higher wind speed
designation.
A code-compliant 90-mph or 60-mph tested asphalt shingle would not
qualify.
Correct?

Eric Haefli

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Jack
Sent: Wednesday, July 21, 2010 9:52 AM
To: codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] CodeTalk Digest, Vol 59, Issue 30

My understanding is as follows:

If a roof was permitted prior to March 1, 2002, then it is not allowed
on
mitigation.  After March 1, 2002, it is allowed.
Above is all counties except HVHZ which is Miami, Dade and Broward.
HVHZ is allowed if permitted after 9/1/1994 and not allowed if prior to
that
date. 
Your customer was in October of 2001, so you were right not to allow
this.
If he is in HVHZ, the 1994 date applies.

Jack B. Harris
Jacbilt Enterprises, Inc.
www.jacbilt.com

-----Original Message-----
From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of
codetalk-request at myfloridacode.com
Sent: Tuesday, July 20, 2010 7:07 PM
To: codetalk at myfloridacode.com
Subject: CodeTalk Digest, Vol 59, Issue 30

Send CodeTalk mailing list submissions to
	codetalk at myfloridacode.com

To subscribe or unsubscribe via the World Wide Web, visit
	http://myfloridacode.com/mailman/listinfo/codetalk
or, via email, send a message with subject or body 'help' to
	codetalk-request at myfloridacode.com

You can reach the person managing the list at
	codetalk-owner at myfloridacode.com

When replying, please edit your Subject line so it is more specific than
"Re: Contents of CodeTalk digest..."


Today's Topics:

   1. Wind Mitigation Verification Inspection (Mark Tyson)
   2. FW: Wind Mitigation Verification Inspection (Mark Tyson)
   3. Re: Wind Mitigation Verification Inspection (Mark Cramer)


----------------------------------------------------------------------

Message: 1
Date: Tue, 20 Jul 2010 18:24:47 -0400
From: "Mark Tyson" <mtyson at wildblue.net>
Subject: [Florida Code Talk] Wind Mitigation Verification Inspection
To: <codetalk at myfloridacode.com>
Message-ID: <0DC99B8AE1D04DAF952E5CF2EAEF999B at yourf5358a91b8>
Content-Type: text/plain; charset="iso-8859-1"

Group,

I need you insight. Last week I did a wind mit inspection on a home
where I
was unable to verify thru procedures that I?m aware of that the roof
covering met the minimum requirement of the 2001 Building Code. ( 3 tab
dimensional Shingles)

 

1) I did a public records search and found the roof covering was
permitted
in October of 2001.

2) The AHJ or the owner had no record of manufacturer of the roof
covering

3) The attachments penetrated the ?? cdx roof sheathing meeting the
minimum
penetration requirement but only 4 attachments per shingle

4) No extra shingles at the site and therefore unable to verify
manufacture

 

Under does the roof covering meet the requirements of the 2001 Building
Code
I checked the box unknown or can not verify

 

My client called today in a rage because his insurance is going to
increase
about $ 1,000 per year and was told by his agent that he picked the
wrong
inspector. With the information provided have I missed something? 

 

 

Regards,

Mark Tyson

 

Tyson Home Inspections

M Tyson Construction LLC.

of  772.489.9648  mb  561.756.3075  fx  772.465.9731

Certified General Contractor #1516843

http://www.TysonHomeInspections.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20100720/88160b8
5/at
tachment-0001.html 

------------------------------

Message: 2
Date: Tue, 20 Jul 2010 18:28:10 -0400
From: "Mark Tyson" <mtyson at wildblue.net>
Subject: [Florida Code Talk] FW: Wind Mitigation Verification
	Inspection
To: <codetalk at myfloridacode.com>
Message-ID: <83FA75EF190A4570A63AF73D0B67D2FE at yourf5358a91b8>
Content-Type: text/plain; charset="iso-8859-1"

Sorry, 130mph zone

 

Regards,

Mark Tyson

 

Tyson Home Inspections

M Tyson Construction LLC.

of  772.489.9648  mb  561.756.3075  fx  772.465.9731

Certified General Contractor #1516843

http://www.TysonHomeInspections.com

 

  _____  

From: Mark Tyson [mailto:mtyson at wildblue.net]
Sent: Tuesday, July 20, 2010 6:25 PM
To: 'codetalk at myfloridacode.com'
Subject: Wind Mitigation Verification Inspection

 

Group,

I need you insight. Last week I did a wind mit inspection on a home
where I
was unable to verify thru procedures that I?m aware of that the roof
covering met the minimum requirement of the 2001 Building Code. ( 3 tab
dimensional Shingles)

 

1) I did a public records search and found the roof covering was
permitted
in October of 2001.

2) The AHJ or the owner had no record of manufacturer of the roof
covering

3) The attachments penetrated the ?? cdx roof sheathing meeting the
minimum
penetration requirement but only 4 attachments per shingle

4) No extra shingles at the site and therefore unable to verify
manufacture

 

Under does the roof covering meet the requirements of the 2001 Building
Code
I checked the box unknown or can not verify

 

My client called today in a rage because his insurance is going to
increase
about $ 1,000 per year and was told by his agent that he picked the
wrong
inspector. With the information provided have I missed something? 

 

 

Regards,

Mark Tyson

 

Tyson Home Inspections

M Tyson Construction LLC.

of  772.489.9648  mb  561.756.3075  fx  772.465.9731

Certified General Contractor #1516843

http://www.TysonHomeInspections.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20100720/d719853
4/at
tachment-0001.html 

------------------------------

Message: 3
Date: Tue, 20 Jul 2010 20:06:28 -0400
From: "Mark Cramer" <mcramer1 at tampabay.rr.com>
Subject: Re: [Florida Code Talk] Wind Mitigation Verification
	Inspection
To: <codetalk at myfloridacode.com>
Message-ID: <01cf01cb2868$910d5130$b327f390$@tampabay.rr.com>
Content-Type: text/plain; charset="iso-8859-1"

Even though the FBC didn?t go into effect until March of 2002, I?ve
heard
that shingle manufacturers were already shipping compliant shingles in
2001.
I think you would be safe assuming they met the requirements in October
2001. 

 

You could always ask the seller to have his roofer provide the
documentation
that the shingles meet the code requirements. 

 

Mark Cramer

Mark Cramer Inspection Services, Inc.

492 20th Ave. 

Indian Rocks Beach, FL 33785

727-595-4211

http://www.BestTampaInspector.com

 

From: codetalk-bounces at myfloridacode.com
[mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Mark Tyson
Sent: Tuesday, July 20, 2010 6:25 PM
To: codetalk at myfloridacode.com
Subject: [Florida Code Talk] Wind Mitigation Verification Inspection

 

Group,

I need you insight. Last week I did a wind mit inspection on a home
where I
was unable to verify thru procedures that I?m aware of that the roof
covering met the minimum requirement of the 2001 Building Code. ( 3 tab
dimensional Shingles)

 

1) I did a public records search and found the roof covering was
permitted
in October of 2001.

2) The AHJ or the owner had no record of manufacturer of the roof
covering

3) The attachments penetrated the ?? cdx roof sheathing meeting the
minimum
penetration requirement but only 4 attachments per shingle

4) No extra shingles at the site and therefore unable to verify
manufacture

 

Under does the roof covering meet the requirements of the 2001 Building
Code
I checked the box unknown or can not verify

 

My client called today in a rage because his insurance is going to
increase
about $ 1,000 per year and was told by his agent that he picked the
wrong
inspector. With the information provided have I missed something? 

 

 

Regards,

Mark Tyson

 

Tyson Home Inspections

M Tyson Construction LLC.

of  772.489.9648  mb  561.756.3075  fx  772.465.9731

Certified General Contractor #1516843

http://www.TysonHomeInspections.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://myfloridacode.com/pipermail/codetalk/attachments/20100720/146a747
5/at
tachment.html 

------------------------------

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
http://myfloridacode.com/mailman/listinfo/codetalk


End of CodeTalk Digest, Vol 59, Issue 30
****************************************

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe by sending an email to
codetalk-unsubscribe at myfloridacode.com
or
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe by sending an email to
codetalk-unsubscribe at myfloridacode.com
or
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk

_______________________________________________
CodeTalk mailing list
CodeTalk at myfloridacode.com
Unsubscribe by sending an email to
codetalk-unsubscribe at myfloridacode.com
or
Unsubscribe or change your options at:
http://myfloridacode.com/mailman/listinfo/codetalk




More information about the CodeTalk mailing list