It appears that you would only require 60" passing space if your sidewalk is over 200' in length.  So your 41" is acceptible as is.  As stated earlier the minimum is only 36".

 

Steve

 

11-4.3.4 Passing space. If an accessible route has less than 60 inches (1525 mm) clear width, then passing spaces at least 60 inches by 60 inches (1525 mm by 1525 mm) shall be located at reasonable intervals not to exceed 200 feet (61 m). A T-intersection of two corridors or walks is an acceptable passing place. 
 


Date: Mon, 8 Mar 2010 15:23:25 -0500
From: FineR at gtlaw.com
To: blemaster at co.okaloosa.fl.us; rich at wayneallenbuilding.com; Bob at contractorsinstitute.com; codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] Handicap route widths








The issue, I believe, may have to do with means of egress.  There are some places that the accessibility statutes (553.501-553-513) specifically require a 44" wide path and these are written into Chapter 11.  Outside of those areas, though, you have to consider whether your accessible route is the means of egress for the guy in the wheelchair.  If it is, then you may need 44" just like other means of egress (including exterior means of egress)-- that's why the ramp has to be 44".  If the path is not the means of egress for the wheelchair and the statute/code does not expressly require the 44", you shouldn't have to do it.
 
Keep in mind that even if you are not exempt from the accessibility code, you are likely subject to the "alterations standards" not new construction standards (it is an existing building, after all).  See 11-4.1.6.  If it is technically infeasible to provide 44", you may not have to do it... just the maximum extent feasible.
 
[BTW:  this was not, and should not be considered legal advice- and is for discussion purposes only]
 
Good luck,
 
Robert
 

Robert S. Fine, Esq., AIA
Environmental, Land Development, Accessibility,
Building and Life Safety Codes Law
Board Certified in Construction Law
Greenberg Traurig, PA
1221 Brickell Avenue
Miami, Florida 33131
Tel: (305) 579-0826
Fax:(305) 961-5826
E-Mail:  FineR at gtlaw.com





     Tax Advice Disclosure: To ensure compliance with requirements imposed by the IRS under Circular 230, we inform you that any U.S. federal tax advice contained in this communication (including any attachments), unless otherwise specifically stated, was not intended or written to be used, and cannot be used, for the purpose of (1) avoiding penalties under the Internal Revenue Code or (2) promoting, marketing or recommending to another party any matters addressed herein.

 
     The information contained in this transmission may contain privileged and confidential information.  It is intended only for the use of the person(s) named above. If you are not the intended recipient,  you are hereby notified that any review, dissemination, distribution or duplication of this communication is strictly prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message. To reply to our email administrator directly, please send an email to postmaster at gtlaw.com.
  



 

From: codetalk-bounces at myfloridacode.com [mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Bill LeMaster
Sent: Monday, March 08, 2010 1:57 PM
To: 'Rich Allen'; 'Bob Koning'; codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] Handicap route widths




If the rise and run is 1:20 it is not considered a ramp. If it is steeper than 1:20 (1:19) then it would be a ramp.
Thank you,
 

William T. LeMaster CBO/CEAP/MCP
Okaloosa County


From: codetalk-bounces at myfloridacode.com [mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Rich Allen
Sent: Friday, March 05, 2010 11:20 AM
To: 'Bob Koning'; codetalk at myfloridacode.com
Subject: Re: [Florida Code Talk] Handicap route widths
 
Thanks Bob. 
 
The original construction is in the 60’s or 70’s but the modifications without a permit have changed the accessibility of the original structure therefore both (ii) & (iii) are enforceable if my interpretation is correct. And if I had to guess there have been other modifications over the years inside the building without a permit that I am unaware due to multiple owner changes over the years.
 
I have a 5’ wide accessible route from the handicap parking space in the parking lot to the top of the ramp. I have a 48” wide ramp with handrails at 1:20 slope for 27’. I have a 5’x5’ level landing at the top of the ramp and the bottom of the ramp. I have a 41” wide level walkway from the bottom landing to the front door of the building. I am stating that per 11-4.3.3 – Accessible Route Width – that the walkway from the landing to the door only has to be 36” minimum not 44” as the 44” requirement is for ramps and parking spaces. Is this a correct interpretation?
Thanks
Rich
 




From: Bob Koning [mailto:Bob at ContractorsInstitute.com] 
Sent: Friday, March 05, 2010 11:38 AM
To: Rich Allen; codetalk at myfloridacode.com
Subject: RE: [Florida Code Talk] Handicap route widths
 
Rich what is the date of ORIGINAL construction for the building. If before Oct, 1997 then all of these are exempt. Follow Federal guidelines, the Building Department cannot enforce the FBC provision upon it:
11-4.1.6 Accessible buildings: Alterations.
 
This edition of the code does not apply to buildings, structures or facilities which were in existence on October 1,1997, unless:
 
(i) The building, structure or facility is being converted from residential to nonresidential or mixed use, as defined by local law.
 
(ii) The proposed alteration or renovation of the building, structure or facility will affect usability or accessibility to a degree which invokes the requirements of Section 303(a) of the ADA of 1990, or
 
(iii) The original construction or any former alteration or renovation of the building, structure or facility was carried out in violation of applicable permitting law:
 
*****
 
If not, the accessible route must be 44” at curb ramps and at accessible parking spaces:
11-4.6 Parking and passenger loading zones. 
 
11-4.6.1 Minimum number. Parking spaces required to be accessible by Section 11-4.1 shall comply with Sections 11-4.6.2 through Section 11-4.6.5. Passenger loading zones required to be accessible by Section 11-4.1 shall comply with Section 11-4.6.5 and 11-4.6.6. 
 
11-4.6.2 Location. Accessible parking spaces serving a particular building shall be located on the shortest safely accessible route of travel from adjacent parking to an accessible entrance. In parking facilities that do not serve a particular building, accessible parking shall be located on the shortest accessible route of travel to an accessible pedestrian entrance of the parking facility. In buildings with multiple accessible entrances with adjacent parking, accessible parking spaces shall be dispersed and located closest to the accessible entrances.
 
(1)                All spaces must be located on an accessible route no less than 44 inches (1118 mm)wide so that users will not be compelled to walk or wheel behind parked vehicles.
 
R.J.Koning - Director
Contractors Institute
rjkoning at contractorsinstitute.com
8301 Joliet Street
Hudson, Fl 34667
727-863-5147
 
 
 


From: codetalk-bounces at myfloridacode.com [mailto:codetalk-bounces at myfloridacode.com] On Behalf Of Rich Allen
Sent: Friday, March 05, 2010 9:50 AM
To: codetalk at myfloridacode.com
Subject: [Florida Code Talk] Handicap route widths
 
Hello Group
 
I have been hired to help a commercial building owner that performed work with out a permit. I have no problem removing and reinstalling items that clearly are wrong but I do not want to waste money on items that do not need to be fixed. The issue is a handicap route from the front door to the parking lot. Due to elevation changes a single ramp is required. There is a 5’x5’ landing at the top and bottom of the ramp. The ramp is 44” wide. The problem is the walkway leading to the ramp is 33’ long and only 41” wide. The current plans reviewer wants the walkway removed and reinstalled to 44” wide and a 5’x5’ “rest area” in the middle of it. The reviewer claims the walkway needs to be 44” wide per code but cannot show me where in the code it says that. I keep going back to 11-4.3.3 that states 36” minimum clear width for an accessible route and the reviewer says that because the ramp the ramp requires 44”, the walkway has to be also. “I have been doing this a long time and this is the way it has to be” per the plans reviewer.
 
At this point I am going to make the changes per the reviewer so the project can move forward but am I correct or the plans reviewer?
Thanks
Rich
 































 		 	   		  
_________________________________________________________________
Hotmail: Trusted email with powerful SPAM protection.
http://clk.atdmt.com/GBL/go/201469227/direct/01/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://myfloridacode.com/pipermail/codetalk/attachments/20100308/395154ca/attachment.html 


More information about the CodeTalk mailing list
| Home | Contractors Institute | Building Official | CI Certified | About Us | Contact Us |
| ©Copyright 2005 Contractors Institute     All rights reserved |